Happy new year I have a question 500 KVA transformer secondary has 6 runs of 600 MCM ABCN with a grounding conductor that's 500 MCM its feeding a 2000 amp frame 1800 AT breaker I need to bond the secondary neutral what size would be code ? This is not a service this is just a transformer which is fed from a switchboard .
Heres what we did using Art 250 took the 6 X 600MCM = 3600 x 12.5 % 450 MCM So my question is this would be a 500 MCM bonding jumper from the metal case ground of that transformer to the neutral bar ?
Heres what we did using Art 250 took the 6 X 600MCM = 3600 x 12.5 % 450 MCM So my question is this would be a 500 MCM bonding jumper from the metal case ground of that transformer to the neutral bar ?