But the same size as which GEC? And what if the wires in the pipes (at least some of them) are bonding jumpers rather than GECs?The bonding jumper should be the same size as the grounding electrode conductor.
But the same size as which GEC? And what if the wires in the pipes (at least some of them) are bonding jumpers rather than GECs?
But the same size as which GEC? And what if the wires in the pipes (at least some of them) are bonding jumpers rather than GECs?
Yes, and the code rule only applies to GECs. While the physics is the same and you should bond it, there is no rule that says you have to, if the conductor is not a GEC.Have you ever seen bonding jumpers run like that?