electrofelon
Senior Member
- Location
 - Cherry Valley NY, Seattle, WA
 
- Occupation
 - Electrician
 
I know we have been over supply-side bonding Jumpers in parallel, and how the code is a little ambiguous on this, not specifically stating the allowance for running supply-side Jumpers in parallel sized to each raceway like grounding electrode conductor taps.  for example let's just take the simple case of a CT cabinet that needs to be bonded "indirectly" from the service panel downstream from it with a SSBJ where there are parallel raceways between the two.  Can I run a single supply-side bonding jumper through 1 of the parallel raceways?  It seems not, since 300.3(B) which specifically mentions bonding conductors.  300.3(B)(2) permits grounding and bonding conductors outside of raceways, but that seems to dance around allowing 1 in a single of parallel raceways.  Do I need to either run outside of the raceways or run a full-sized in each one?
	
		
			
		
		
	
				
			
				