T thleone New member Jan 26, 2005 #1 Where in the NEC does it state that 4" seal tight (liquid tight)flexable conduit must contain an external equipment bonding jumper? Is this correct? [ January 26, 2005, 09:56 AM: Message edited by: thleone ]
Where in the NEC does it state that 4" seal tight (liquid tight)flexable conduit must contain an external equipment bonding jumper? Is this correct? [ January 26, 2005, 09:56 AM: Message edited by: thleone ]
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jan 26, 2005 #2 Re: bonding jumpers on sealtight flex There is no requirement that the bonding jumper be external, but LFMC of that size is not suitable for use as an EGC. [250.118(7), 350.60, and 250.102(E)] Don
Re: bonding jumpers on sealtight flex There is no requirement that the bonding jumper be external, but LFMC of that size is not suitable for use as an EGC. [250.118(7), 350.60, and 250.102(E)] Don