Where in the NEC does it state that 4" seal tight (liquid tight)flexable conduit must contain an external equipment bonding jumper?

Is this correct?

[ January 26, 2005, 09:56 AM: Message edited by: thleone ]
 
Re: bonding jumpers on sealtight flex

There is no requirement that the bonding jumper be external, but LFMC of that size is not suitable for use as an EGC. [250.118(7), 350.60, and 250.102(E)]