Bonding locknut or bushing

Status
Not open for further replies.

elecmen

Senior Member
Location
NH
Occupation
Electrician
Is a bonding locknut or bushing required on a offset nipple between a meter socket and disconnect when a myers hub is used on the disconnect end? Please give code reference. Thanks
 
So what your saying is if one end is threaded into the myers hub than it is bonded?
 
Just to cover one way out in left field possibility. Only one end needs to be bonded, as long as you have a grounded conductor.
In this case you are simply bonding the service raceway (offset nipple).
The meter and service diconnect are bonded by the grounded conductor
 