I have received informal pushback from construction teams for requiring conduit bonding to cable tray for LV telecom raceway infrastructure. The way I interpret the code is that all of that raceway infrastructure shall be electrically continuous back to the TGB. This means every 1" conduit for a runout to the data outlets on the floor needs to be bonded to the cable tray. The cable tray sections are bonding to be electrically continuous and that cable tray system is connected to the telecom ground bar.
Owners are hearing that this is a waste of time and money and there are plenty of installations (right or wrong) that don't follow this strategy.
To me, the code is written around power circuits but there is no exception or clarification for voltage level to dismiss LV raceway. Am I in the right or am I requiring grounding and bonding that is above and beyond? Thanks for the input.
Owners are hearing that this is a waste of time and money and there are plenty of installations (right or wrong) that don't follow this strategy.
To me, the code is written around power circuits but there is no exception or clarification for voltage level to dismiss LV raceway. Am I in the right or am I requiring grounding and bonding that is above and beyond? Thanks for the input.