bonding metal skin of wood frame building

Status
Not open for further replies.

stew

Senior Member
Weecently had an inspector require a bond of the metal skin of a wood frame building. According to one of mikes recent newsletters this is not required,desiable but not required. Where does the specific code reference for not being required reside?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: bonding metal skin of wood frame building

Originally posted by stew:
Where does the specific code reference for not being required reside?
No such code section.

What the inspector would have to show you is a section that requires the metal skin of wood frame building to be bonded.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Re: bonding metal skin of wood frame building

Originally posted by iwire:
Originally posted by stew:
Where does the specific code reference for not being required reside?
No such code section.

What the inspector would have to show you is a section that requires the metal skin of wood frame building to be bonded.
Originally posted by benaround:
250.4 a(4)

frank
Okay, then the inspector will have to show you how the building is likely to become energized.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: bonding metal skin of wood frame building

Originally posted by benaround:
250.4 a(4)

frank
Frank are you suggesting the metal skin on a wood frame building is likely to be energized?

I think that is a stretch and a half.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Re: bonding metal skin of wood frame building

Originally posted by benaround:
Doorbell button.

frank
If I'm not mistaken, 16 volts is not high enough to require bonding.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: bonding metal skin of wood frame building

Frank in my opinion the most likely things to energize the metal skin of a wood frame building would be the service equipment which is all required to be bonded already.

Or perhaps outdoor outlets mounted on this metal skin, again those would be bonded already.

Another question that comes to mind is how many bonds would be required, would I have bond the siding once then place a bonding jumper between each section?

Bob

[ July 11, 2005, 08:40 PM: Message edited by: iwire ]
 

benaround

Senior Member
Location
Arizona
Re: bonding metal skin of wood frame building

I had that coming, just didn't know by whole forum!

Actually when I was a kid I got knocked on my butt from a house with alum. siding and I guess I still haven't got over it.

DOORBELL LMFAO

[ July 11, 2005, 11:20 PM: Message edited by: benaround ]
 

physis

Senior Member
Re: bonding metal skin of wood frame building

I had that coming, just didn't know by whole forum!
Wait a minute, I haven't said anything yet. :D

I have to look in on more of these threads, you never know what you'll miss. :D
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: bonding metal skin of wood frame building

Even if you wanted to bond the skin of a metal building, how would you do it? The normal installation methods does not provide an electrical connection between each of the pieces of the metal skin, so you would have to bond each piece individually.
Don
 

stud696981

Senior Member
Re: bonding metal skin of wood frame building

I'm not trying to knock inspectors, I know there are a lot of good ones out there. Unless your town has a code that says to bond siding, this is a good example of an inspector abusing his authority or just not having a clue on what his job really is.
 

macmikeman

Senior Member
Re: bonding metal skin of wood frame building

What if that metal skinned wood framed building had a swimming pool within 5 ' of it?. I bet you would then see multiple bonding connections on the sections near the pool.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: bonding metal skin of wood frame building

Originally posted by macmikeman:
What if that metal skinned wood framed building had a swimming pool within 5 ' of it?. I bet you would then see multiple bonding connections on the sections near the pool.
In that case I guess you would be bonding the siding or telling the people to cover it with new vinyl siding.
 