If there are no grounding electrodes on premises and a 200 amp 120/240v service is installed, there would be a made electrode with two ground rods driven and a #6 cu jumped between the two and attached to the system neutral.
250.104(A). What would be the size of the bonding jumper to the metal water piping? Would it be based of 250.102(C)(1) which would be #4 cu ? Or would it be based some how from 250.104(B) which directs you to 250.122 #6 cu?
Or none of the above?
To add on. Just checking that when sizing for the GEC, I should look at the 250.66 chart and 1100kcmil and ANY WIRE SIZE OVER is a 3/0 cu gec.
250.102(C)(1) is strictly bonding and jumping, and has nothing to do with gec.
Thank you
250.104(A). What would be the size of the bonding jumper to the metal water piping? Would it be based of 250.102(C)(1) which would be #4 cu ? Or would it be based some how from 250.104(B) which directs you to 250.122 #6 cu?
Or none of the above?
To add on. Just checking that when sizing for the GEC, I should look at the 250.66 chart and 1100kcmil and ANY WIRE SIZE OVER is a 3/0 cu gec.
250.102(C)(1) is strictly bonding and jumping, and has nothing to do with gec.
Thank you