At this point it is clear the code allows you to splice in conduit bodies if they are marked by the manufacturer with their volume. My question is for metalic conduit bodies. Once you make a splice in one doesn't atricle 250.148 (c) which requires a connection by grounding device between the box and EGC's come into play? I have not seen a conduit body with provisions for a ground screw and am not sure how to meet this requirement.
 
250.148 Continuity and Attachment of Equipment
Grounding Conductors to Boxes. Where circuit conductors
are spliced within a box, or terminated on equipment
within or supported by a box, any equipment grounding conductor(
s) associated with those circuit conductors shall be connected
within the box or to the box with devices suitable for
the use in accordance with 250.148(A) through (E).

A conduit body is not a box.
 