Bonding Metallic Raceways Connected to Nonmetallic Equipment
shortcircuit2
South of Bawstin
314.3 requires internal (Ex No.1) or integral bonding means (Ex No. 2) when metal raceways or metal-armored cables are used with nonmetallic boxes.
Why is there no Code requirement for internal or integral bonding means for metal raceways or metal-armored cables used with nonmetallic equipment enclosures?
Even in a non metallic equipment enclosure isn’t there a bonding screw point or grounding screw point? If not, don’t you still treat it like a box, by tying grounds together, including using grounding bushings for metal conduits?
I don't see any requirement in the Code to bond the metal raceway or metal wiring method to the ground bar inside the nonmetallic equipment enclosure. 314.3 applies to boxes.
I guess 250.4(A)(5) is the only section I can find that may apply. There would be lower impedance if the metal raceway or metallic wiring method was bonded at the nonmetallic equipment enclosure.