Bonding Metallic Raceways Connected to Nonmetallic Equipment

Status
Not open for further replies.

shortcircuit2

Senior Member
Location
South of Bawstin
314.3 requires internal (Ex No.1) or integral bonding means (Ex No. 2) when metal raceways or metal-armored cables are used with nonmetallic boxes.

Why is there no Code requirement for internal or integral bonding means for metal raceways or metal-armored cables used with nonmetallic equipment enclosures?
 
Even in a non metallic equipment enclosure isn’t there a bonding screw point or grounding screw point? If not, don’t you still treat it like a box, by tying grounds together, including using grounding bushings for metal conduits?
 
I don't see any requirement in the Code to bond the metal raceway or metal wiring method to the ground bar inside the nonmetallic equipment enclosure. 314.3 applies to boxes.

I guess 250.4(A)(5) is the only section I can find that may apply. There would be lower impedance if the metal raceway or metallic wiring method was bonded at the nonmetallic equipment enclosure.
 