I have a 24kw generac Im installing for a client, once the service rated ats goes in I will have to do all my GEC and bonding jumper inside that enclosure, slight dilemma is that there is a I believe water/gas bond, and ufer that is in the panel (circled in red). From me research in the code and some contact Mike holt put out I see nothing wrong with splicing those and extending them or just bringing an oversized EGC from the transfer switch (#4cu in this case) and then land them all on the same ground bar, I think the intent would be the same. Does anybody see any issues with this?