M menaelec New member May 5, 2006 #1 When installing a generator on a dredge, am I correct in NOT bonding the generator neutral to the ground bus in the switchgear?
When installing a generator on a dredge, am I correct in NOT bonding the generator neutral to the ground bus in the switchgear?
petersonra Senior Member Location Northern illinois Occupation engineer May 5, 2006 #2 Re: Bonding neutral of shipboard generator to ground menaelec said: When installing a generator on a dredge, am I correct in NOT bonding the generator neutral to the ground bus in the switchgear? Click to expand... a lot of ships use ungrounded power. i think you will need to discuss this with the ship's chief engineer.
Re: Bonding neutral of shipboard generator to ground menaelec said: When installing a generator on a dredge, am I correct in NOT bonding the generator neutral to the ground bus in the switchgear? Click to expand... a lot of ships use ungrounded power. i think you will need to discuss this with the ship's chief engineer.