I recently replaced a small 100A residential panel with a larger 100A panel. The panel is located several feet from the meter therefore a service disconnect is mounted next to the meter socket and joined via a nipple. The service wires to the panel are from the service disconnect are run inside a length of IMC. The neutral in the panel is not bonded to the panel and a ground bar is used for equipment grounding. When I looked at the service disconnect I didn?t notice a ground rod or wire suggesting that the service was grounded. I opened the service disconnect and the meter socket and found that the neutral was not bonded inside the disconnect but rather inside the meter socket and a ground wire inside ran from the neutral down the incoming pipe (underground feed) to ground. Does the neutral in the service disconnect still need to be bonded and a ground rod driven? Also, the original panel had the neutral bonded to the panel and being that the service disconnect was bonded to the panel through the conduit could this potentially create objectionable current by supplying more than one path for neutral current to ground?