Bonding of 24VDC instrument junction box

Dale001289

Senior Member
Location
Georgia
Recently, the inspector cited junction boxes that were not bonded. He said the shield on the circuits could be used for bonding the box. However, there are two 3/4" LFMC attached to the box with locknuts on the inside. LFMC is a recognized EGC per 250.118, so why cant this be considered sufficient bonding for the box?
 
Recently, the inspector cited junction boxes that were not bonded. He said the shield on the circuits could be used for bonding the box. However, there are two 3/4" LFMC attached to the box with locknuts on the inside. LFMC is a recognized EGC per 250.118, so why cant this be considered sufficient bonding for the box?
I think the inspector is wrong. You do not want to use the shield as a bonding conductor. For one thing it is way too small. The smallest bonding conductor allowed is #14.
 
I think the inspector is wrong. You do not want to use the shield as a bonding conductor. For one thing it is way too small. The smallest bonding conductor allowed is #14.

Agreed - I’ve never seen one done like that either


Sent from my iPhone using Tapatalk
 
Let me ask another question. These are probably class 2 circuits. Is there any code requirement to actually run an EGC with class 2 circuits?

The circuits come off a class 1 power supply in the PLC which my understanding is they automatically default to class 1 but they are all 24VDC


Sent from my iPhone using Tapatalk
 
If your 24VDC is separately derived and ungrounded then the only thing accomplished by bonding the box is to ensure that if there's a fault in the box then everything else bonded to the box becomes energized at 24V to the other DC conductor. Seems low stakes and pretty ticky-tack on the part of the inspector.

I suppose 250.4(A)(3) still requires the box to be bonded though. 🤷🏻‍♂️
 
The circuits come off a class 1 power supply in the PLC which my understanding is they automatically default to class 1 but they are all 24VDC


Sent from my iPhone using Tapatalk
I think if you look very closely at what the code says, they are still class 2 circuits.
 
We haven't established that his power source has those limits. I agree there's a good chance you're right, but the code does not say that a Class 1 power source becomes Class 2 just because it's part of a PLC.
 
If your 24VDC is separately derived and ungrounded then the only thing accomplished by bonding the box is to ensure that if there's a fault in the box then everything else bonded to the box becomes energized at 24V to the other DC conductor. Seems low stakes and pretty ticky-tack on the part of the inspector.

I suppose 250.4(A)(3) still requires the box to be bonded though.

I don’t think a PLC power supply would be considered a separately derived system


Sent from my iPhone using Tapatalk
 