If all conductors pass through boxes, metal wireways, and other metal enclosures with no splices or terminations, is the box or enclosure required to be bonded with a wire type EGC?
 
If the raceway is metallic and qualifies as an EGC then as Augie stated no. If the raceway is non-metallic or does not qualify as an EGC then yes.
 