• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

bonding of boxes and enclosures

Merry Christmas
Status
Not open for further replies.

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
If all conductors pass through boxes, metal wireways, and other metal enclosures with no splices or terminations, is the box or enclosure required to be bonded with a wire type EGC?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the raceway is metallic and qualifies as an EGC then as Augie stated no. If the raceway is non-metallic or does not qualify as an EGC then yes.
 