Bonding of communication conduits in Healthcare facilities

Status
Not open for further replies.

fjohn49

Member
An inspector has required the bonding of conduit stubs for telephone cables in patient care areas. He is using Article 517.80 as his basis for requiring that these stub outs be bonded. I do not understand his interpretation.

VI. Communications, Signaling Systems, Data Systems, Fire Alarm Systems, and Systems Less Than 120 Volts, Nominal

517.80 Patient Care Areas.

Equivalent insulation and isolation to that required for the electrical distribution systems in patient care areas shall be provided for communications, signaling systems, data system circuits, fire alarm systems, and systems less than 120 volts, nominal.

FPN: An acceptable alternate means of providing isolation for patient/nurse call systems is by the use of nonelectrified signaling, communications, or control devices held by the patient or within reach of the patient
 
Status
Not open for further replies.
Top