Bonding of conductor to a Cable tray

Status
Not open for further replies.
We have a tray at the roof which is in direct contact with lightning down conductor, touching each other, can we bond this?Would this have and effect to the low voltage equipment grounding system just in case lightning strikes and hit the arrester?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: Bonding of conductor to a Cable tray

My take on this is that it probably does not matter much if you bond them together or not. if lightning hits the roof of your building, it is just as likely to jump to the cable tray regardless of whether it is bonded or not to the air electrode downwire or not.

It would appear from this FPN, that you may have to bond them. I think you would need to consult the referenced std.

250.106 FPN No. 2: Metal raceways, enclosures, frames, and other non?current-carrying metal parts of electric equipment installed on a building equipped with a lightning protection system may require bonding or spacing from the lightning protection conductors in accordance with NFPA 780-1997, Standard for the Installation of Lightning Protection Systems. Separation from lightning protection conductors is typically 1.8 m (6 ft) through air or 900 mm (3 ft) through dense materials such as concrete, brick, or wood.
 