I'm looking for some opinions here...
The equipment being installed is European which has US approvals. The smoke detectors are supplied by the manufacture as a plastic box and fall under the fire alarm device listing. Like all modern day fire alarm systems I'm familiar with, the system is less than 50 volts. I have to be honest, I don't think I'll ever have a good understanding on what defines the "Class" of power supply, but for now I'm assuming it's a Class 1 power supply (maybe someone can provide a link to educate me on that point).
My references are to the 2011 edition of NFPA 70.
I'm concerned about 314.3 which requires the plastic box to have an internal means of bonding the conduit entries, which this box does not have. Article 314.3 or 4 don't address bonding or grounding requirements as to me this would be the function of 250.86. I have to ask...should 314.3 have a similar reference to 250.112(I), that 314.4 has?
Is my conclusion that the use of the plastic "Manufacture Supplied" box is acceptable for use with the metal conduit, even without the internal bonding method?
The equipment being installed is European which has US approvals. The smoke detectors are supplied by the manufacture as a plastic box and fall under the fire alarm device listing. Like all modern day fire alarm systems I'm familiar with, the system is less than 50 volts. I have to be honest, I don't think I'll ever have a good understanding on what defines the "Class" of power supply, but for now I'm assuming it's a Class 1 power supply (maybe someone can provide a link to educate me on that point).
My references are to the 2011 edition of NFPA 70.
- NEC 250.112(I) does not require conduit to be grounded when the circuit is less than 50 volts and is supplied from a Class 1 power supply (i.e. the fire alarm step down transformer).
- NEC 250.86, which addresses “Conductor Enclosures and Raceways” requires conduits to be grounded with the exception of fire alarm systems, due to it’s reference to 250.112(I).
- NEC 314.3 permits the use of “nonmetallic” boxes but when used with metal raceways, requires a “…internal bonding means…between all entries…”. This section doesn’t say either the box or the conduit has to be grounded. That requirement would fall under 250.86, which permits their exclusion based on 250.112(I).
- NEC 314.4 does not require metal boxes to be grounded due to it’s reference to 250.12(I).
I'm concerned about 314.3 which requires the plastic box to have an internal means of bonding the conduit entries, which this box does not have. Article 314.3 or 4 don't address bonding or grounding requirements as to me this would be the function of 250.86. I have to ask...should 314.3 have a similar reference to 250.112(I), that 314.4 has?
Is my conclusion that the use of the plastic "Manufacture Supplied" box is acceptable for use with the metal conduit, even without the internal bonding method?