bonding of covers

Status
Not open for further replies.

kujawata

New member
Should cast iron manhole covers and/or metal handhole covers be bonded when used as an access cover over a concrete enclosure?
 
Re: bonding of covers

Bob,
I don't think that the word "likely" is involved in the answer to this question. It is my opinion that 250.4(A)(3) requires bonding.
Don
 
Re: bonding of covers

Originally posted by don_resqcapt19:
Bob,
I don't think that the word "likely" is involved in the answer to this question. It is my opinion that 250.4(A)(3) requires bonding.
Don
I guess I was thinking more along the lines of 250.4(A)(4).

I'm not sure (3) would apply.

Is conduit considered to be electrical equipment?

Equipment. A general term including material, fittings, devices, appliances, luminaires (fixtures), apparatus, and the like used as a part of, or in connection with, an electrical installation.

One might be inclined to think from this definition that raceways are not equipment.

And can you stretch the meaning of the word "enclose" to include such a lid? the lid certainly does not enclose anything by itself.

Enclosed. Surrounded by a case, housing, fence, or wall(s) that prevents persons from accidentally contacting energized parts.
 
Re: bonding of covers

I agree with Don.

A general term including material, fittings
To me it's hard to imagine anything that doesn't qualify.

Non-current carrying conductive materials enclosing electrical......

I think a cover encloses.
 
Re: bonding of covers

Intuitively, I agree with Don. As for the Code, well...I agree with Don here too that 250.4(A)(3) applies. If you look carefully at the wording of 250.4(A)(3), it says "... equipment, or forming part of such equipment ...". IMO, that means the cover to the enclosure as well. That being said, of the few manhole and handhole covers I have taken off, I don't remember seeing a bond anywhere, but I guess I wasn't looking for it at the time. :)
 