Disregard the termination of the first disconnect- it was changed after the picture was taken!
This is a 600-amp service that a j-man put together that I work with.
My question is about the bonding.
Each of the 3 disconnects have their bonding screw installed. There is a 6-lug ground bar located in the CT can that a #4 ground wire from each disconnect goes to.
To the left of the CT can (out of picture) is the meter and a #4 ground wire from there goes to the ground bar in the can. Also, the ufer ground GEC comes to the can from the house.
My question basically is that the neutral terminal block in the can is also bonded to the can. It seems to me that there is the issue of objectional current on the #4 ground wire because it’s basically creating a parallel path for neutral current. But I also understand that if you have a fault in the can you need a return path back to the transformer.
The J-man and I were having a discussion about this bonding today before the poco came to hook it up.
What are your thoughts about this setup?
Thanks