Article 250.104B states
Quote:
(B) Other Metal Piping, Where installed in or attached to abuilding or structure, metal piping system(s), including gas piping, that may become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used...
Wouldn't all gas pipe have the potential to become energized? If I bond the structural steel would the gas pipe ,supported by metal hangers and fasteners, be adequate? Is it best to bond the gas pipe or is it something that is rarley enforced. I guess that it is best to have all metal to have the same potential to earth. Thank you for your time and effort.
Justin
Quote:
(B) Other Metal Piping, Where installed in or attached to abuilding or structure, metal piping system(s), including gas piping, that may become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used...
Wouldn't all gas pipe have the potential to become energized? If I bond the structural steel would the gas pipe ,supported by metal hangers and fasteners, be adequate? Is it best to bond the gas pipe or is it something that is rarley enforced. I guess that it is best to have all metal to have the same potential to earth. Thank you for your time and effort.