Bonding of Isolated Grounding system to plant electrode system, i.e. ground loop

Status
Not open for further replies.

Dale001289

Senior Member
Location
Georgia
Is it permissible to have a removable link installed between an Isolated grounding system i.e., underground copper conductor off a Triad and point where it ties into the Plant grounding electrode system, i.e. ground ring?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Is it permissible to have a removable link installed between an Isolated grounding system i.e., underground copper conductor off a Triad and point where it ties into the Plant grounding electrode system, i.e. ground ring?

There is no requirement that an EGC be continuous.

However I'm not sure that what you are describing is even code legal. The so-called isolated ground goes back to the EGC at the service point not to the grounding electrode system.
 

Smart $

Esteemed Member
Location
Ohio
There is no requirement that an EGC be continuous.

However I'm not sure that what you are describing is even code legal. The so-called isolated ground goes back to the EGC at the service point not to the grounding electrode system.
The so-called isolated ground goes back to a common EGC point not to the grounding electrode system. Quite often the common EGC point is the EGC/MBJ point at the service.

@Dale001289
The electrode triad can be tied to any point on the EGC system, or it can be tied directly to the grounding electrode system (GES). However, once the triad is in place, it must be and remain connected.
 

Dale001289

Senior Member
Location
Georgia
The so-called isolated ground goes back to a common EGC point not to the grounding electrode system. Quite often the common EGC point is the EGC/MBJ point at the service.

@Dale001289
The electrode triad can be tied to any point on the EGC system, or it can be tied directly to the grounding electrode system (GES). However, once the triad is in place, it must be and remain connected.


Smart: Your last sentence is where I want to focus. The triad will remain connected, however, the 'removable link' constitutes a gap between the triad and point where all other grounding cables connect. To me, this would be violation of 250.50, however, 250.6(B) seems to allow it - then there's 250.8(A) to consider...I'm so confused (looking at 2017 NEC handbook)
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Smart: Your last sentence is where I want to focus. The triad will remain connected, however, the 'removable link' constitutes a gap between the triad and point where all other grounding cables connect. To me, this would be violation of 250.50, however, 250.6(B) seems to allow it - then there's 250.8(A) to consider...I'm so confused (looking at 2017 NEC handbook)

Any part of the grounding electrode system can be removable other than the one required by 250.64(C) to be continuous. Look at 250.70.
 

Smart $

Esteemed Member
Location
Ohio
Any part of the grounding electrode system can be removable other than the one required by 250.64(C) to be continuous. Look at 250.70.
Removable, yes... provided minimum or required electrodes are maintained. Electrodes have to physically be removed or otherwise rendered 'not an electrode'. They cannot just be disconnected. But Dale wanting a removable link suggests to me he does not want to remove the triad electrodes.

@Dale001289
Exactly what are you seeing as objectionable current requiring the application of 250.6(B)? How would 'unlinking' the triad result in stopping objectionable current that isn't also and will remain on the GES in general?
 

Dale001289

Senior Member
Location
Georgia
Removable, yes... provided minimum or required electrodes are maintained. Electrodes have to physically be removed or otherwise rendered 'not an electrode'. They cannot just be disconnected. But Dale wanting a removable link suggests to me he does not want to remove the triad electrodes.

@Dale001289
Exactly what are you seeing as objectionable current requiring the application of 250.6(B)? How would 'unlinking' the triad result in stopping objectionable current that isn't also and will remain on the GES in general?


The sole connection to plant grounding system as required by 250.50 can result both common mode noise and objectionable currents. The removable link allows the field to 'trouble-shoot' the isolated grounding system and theoretically eliminate both.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The sole connection to plant grounding system as required by 250.50 can result both common mode noise and objectionable currents. The removable link allows the field to 'trouble-shoot' the isolated grounding system and theoretically eliminate both.

A single connection (as in sole) of the GES does not cause a ground loop, ground loops are caused by multiple connections. Your best solution would be to remove the "magical triad".

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Mainly it's about common mode noise - not a loop
So why not provide a link to the isolated ground system in the service equipment where it can be accessed for testing? As mentioned in post #2, this isolated EGS should not connect to the GES itself.

Roger
 

Dale001289

Senior Member
Location
Georgia
I agree the 'link' should occur in an accessible location. I just have to convince the client his idea is not a good one.


Sent from my iPhone using Tapatalk
 

Smart $

Esteemed Member
Location
Ohio
The sole connection to plant grounding system as required by 250.50 can result both common mode noise and objectionable currents. The removable link allows the field to 'trouble-shoot' the isolated grounding system and theoretically eliminate both.
Mainly it's about common mode noise - not a loop
I agree the 'link' should occur in an accessible location. I just have to convince the client his idea is not a good one.
All I see is someone looking for a reason to leave the EGS and the triad disconnected, i.e. completely isolate the equipment from the EGS. Doing so violates the listing for all equipment furnished with a ground prong or terminal.
 

Dale001289

Senior Member
Location
Georgia
Bonding of Isolated Grounding system to plant electrode system, i.e. ground loop

Smart-clientes love to do this . They hate the fact that a 'noisy, dirty' GES is connected to their precious DCS and PLC shields - i.e. isolated GES or Triad
Unfortunately doing so is a violation of 250.50


Sent from my iPhone using Tapatalk
 

Smart $

Esteemed Member
Location
Ohio
Smart-clientes love to do this . They hate the fact that a 'noisy, dirty' GES is connected to their precious DCS and PLC shields - i.e. isolated GES or Triad
Unfortunately doing so is a violation of 250.50
It's a bleed over from one particular type of IEC grounding that is permitted. Tell them to get a backbone and do it the American way. :lol:
 

Dale001289

Senior Member
Location
Georgia
It's a bleed over from one particular type of IEC grounding that is permitted. Tell them to get a backbone and do it the American way. :lol:


I will do everything I can to convince them. The 'removable link' will be removed and will NEVER find its way home again.
 