If installed "Listed" liquidtight flexible metal conduit (LFMC (Art. 350)) complies with the following requirements [250.118(6)(a)-(e)] I understand that NEC will allow the LFMC to be used as an Equipment Grounding (Bonding) Conductor:
(1) The conduit terminates in fittings listed for grounding.
(2) For trade sizes ⅜ inch through ? inch, the circuit conductors are protected by overcurrent devices rated 20A or less.
(3) For trade sizes ? inch through 1? inch, the circuit conductors are protected by overcurrent devices rated 60A or less.
(4) The combined length of the conduit in the same ground return path doesn't exceed 6 feet.
(5) The application requires flexibility.
Question: If the length of LFMC exceeds 6 feet, and a correctly sized EGC is installed through the LFMC, and correctly terminated at each end in a junction box, and the installation complies with 1-5 above, is an external bonding jumper required on the outside of the LFMC?