Bonding of metal raceways

Status
Not open for further replies.

kstanton5

Member
My question is this. At the main distribution panel the bottom is completely open for conduit entry. All pipes coming thru slab are rigid metal conduit that transition to schedule 40 pvc below. Do all of the pipes require bonding bushings?
 
kstanton5 said:
At the main distribution panel the bottom is completely open for conduit entry. All pipes coming thru slab are rigid metal conduit that transition to schedule 40 pvc below. Do all of the pipes require bonding bushings?

Yes, without a doubt each one is required to be bonded.

250.92
 