250.104(A)(1) requires bonding of metal water piping installed in or on a structure, to one of several elements of the grounding system. No problem.
We have a multi-occupancy structure (apartment building) where the copper water mains are being replaced with CPVC mains, since the copper is springing leaks everywhere. This will metallically isolate the copper piping in the apartments, which will remain, from the existing bonding connection which is via the copper mains, as was required by 250.104(A)(1).
250.104(A)(2) addresses multiple occupancy buildings, and permits the bonding of the now-metallically isolated piping to the equipment grounding terminal of the switchgear, switchboard or panelboard supplying that occupancy.
Is the bonding of the metallic water piping in the apartments, now isolated by the CPVC water mains, required to be bonded to one the listed elements? Or does 250.104(A)(2) trump 250.104(A)(1) in this case of multiple occupancies with metallically isolated piping??? Is the bonding merely permitted, and NOT required?
We have a multi-occupancy structure (apartment building) where the copper water mains are being replaced with CPVC mains, since the copper is springing leaks everywhere. This will metallically isolate the copper piping in the apartments, which will remain, from the existing bonding connection which is via the copper mains, as was required by 250.104(A)(1).
250.104(A)(2) addresses multiple occupancy buildings, and permits the bonding of the now-metallically isolated piping to the equipment grounding terminal of the switchgear, switchboard or panelboard supplying that occupancy.
Is the bonding of the metallic water piping in the apartments, now isolated by the CPVC water mains, required to be bonded to one the listed elements? Or does 250.104(A)(2) trump 250.104(A)(1) in this case of multiple occupancies with metallically isolated piping??? Is the bonding merely permitted, and NOT required?