Bonding of motor frame via the buried ground 'loop'

Dale001289

Senior Member
Location
Georgia
There are some here on site that think an additional, external bonding conductor, i.e. #2AWG, #2/0, or #4/0, from the (equipotential) grounding grid 'loop' is required to each motor frame.
From what I can determine per NEC, the motor frame is already bonded via the EGC in the motor termination box and an external bond is not required.
Comments?
 
There are some here on site that think an additional, external bonding conductor, i.e. #2AWG, #2/0, or #4/0, from the (equipotential) grounding grid 'loop' is required to each motor frame.
From what I can determine per NEC, the motor frame is already bonded via the EGC in the motor termination box and an external bond is not required.
Comments?

The additional bonding from the loop to the motor frame is not required by NEC.
This would be a client or specification option


Sent from my iPhone using Tapatalk
 
It is a common industrial specification, likely dating back to the extensive use of ungrounded systems in industrial facilities, years ago.
However as others have said not required by the code. If it is a project specification, just include the costs in the project and add to your profit.
 
Could be use specific. If it is a pool pump motor, it needs an external bonding lug. Not sure for barn application where there is an equipotential grid in the floor. Under normal use cases, I would expect it to make no difference.
 