Fordean
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
Last edited:
I agree with beanland but note that it is commonplace with all the area POCOs to allow/use the grounded conductor to bond the CT meter enclosure or any other POCO cabinet..
Equipment grounding, isolated or otherwise, is normally not introduced prior to the service cabinet here. Code not withstanding, POCO normally does not want to give you a reason to enter their enclosures
I tried to zoom in on the image but could not read any of the print when I did so.
I am assuming the second from far right box is the service disconnect from what I can tell, and is serving the meter bank to it's immediate left, and another (possibly unmetered?) disconnect to the far right.
You are apparently adding all the equipment to the left of the mentioned meter bank but will be CT metering this load.
The question becomes where is the service point? Even though the POCO puts seals on the meters in the meter bank, in most cases that meter bank is still customers equipment and on the NEC side of the service point.
Same would apply to the CT meter equipment. It is likely on the NEC side of the service point, so separation of grounded and equipment grounding conductors should apply since it is on load side of service disconnecting means. But POCO can still lock the CT equipment cabinet as the contained equipment is essentially theirs.
Let me know if I have the arrangement of things wrong - it is too hard to read so I am just guessing at what you have.
For some reason the site has changed uploading of pictures. I dont know why it post a picture. Just trying to load a pdf. File to view.
The picture/image in the pdf appears cropped compared to the image in the OP... but at least we can read the available annotations.Ok I think it was me. Found another way to up load I think
The picture/image in the pdf appears cropped compared to the image in the OP... but at least we can read the available annotations.
The 1200A main appears to be the service disconnect... but needs to be verified it is not a POCO-controlled or required "meter disconnect". Same goes for the disconnect to the immediate right of the CT cabinet.
Ultimately, if the service disconnect is load side of the CT cabinet, bonding is to the grounded conductor. If the service disconnect is to the line side of CT cabinet, bonding is done by EGC isolated from grounded conductor.
If the service disconnect is to the line side of CT cabinet, bonding is done by EGC isolated from grounded conductor.
400 amp is on line side of CT. So I must Isolate Grounded conductor from EGC. ? CT come Pre bonded. Lugs.
In my area no, we would not modify the CT cabinet, we would let the neutral remain bonded.
For some reason the site has changed uploading of pictures. I dont know why it post a picture. Just trying to load a pdf. File to view.
Isn't a CT cabinet nothing more than a cabinet, and you install CT's, grounding lugs, other accessories in it?
I believe there is an exception somewhere that allows neutral to be grounded to a meter socket cabinet
Do they have some jumper bar that bridges between the lug assemblies that the CT's wrap around?Not in my area.
Here we must use what the power company requires and here that is a CT cabinet like this.
![]()
The neutral lugs will be directly attached to the enclosure.
Do they have some jumper bar that bridges between the lug assemblies that the CT's wrap around?
Most of what we see around here is POCO supplied and usually POCO installed, but often is just a cabinet and they mount CT's in the field (or in the shop, but not preinstalled from mfgr.) They will pass field installed conductors directly through the CT's and make splices with Polaris taps or similar devices.