I upgraded the service on an old triplex with a "four meter socket + mains" enclosure feeding new subpanels for each of the units + the house panel. There is no single main for the whole service there are essentially four main breakers for each of the sub panels. The service is 120/240 single phase, the feeders are 3/0.
The neutral buss is bonded to the can in the
meter(s)/mains(s) enclosure. I did not bond the neutral buss(s) in the sub panels to their enclosures, because I learned that you only do that once at the main neutral buss. The inspector says I have to bond the neutral buss at each sub panel. I say not. What do you think?