If this indoors the 100' is a problem.I am trying to see where it says in NEC, maybe a picture of how after a transformer, ( separately derived system), you bond the XO in the transformer, the first disconnect is 100' away, does the disconnect get bonded?
You can bond the neutral either at the transformer or at the panel but as Larry stated never both. We always bond the neutral at the transformer. As texie stated your 100 feet of secondary conductors is probably a violation.I am trying to see where it says in NEC, maybe a picture of how after a transformer, ( separately derived system), you bond the XO in the transformer, the first disconnect is 100' away, does the disconnect get bonded?