Bonding of single phase transformer

Merry Christmas

icooperjr

New User
Location
Charlotte
Occupation
Electrical
If I have a Single Phase 7.5 kva Transformer with a primary voltage of 480 volts (H1, H2) and the secondary voltage is 208 volts phase to phase (X1-X2) for a 208 volt Split unit Air conditioner. On the secondary side of the transformer, I have X1 and X2. Upon the bonding of X2 to the bonding terminal/ Grounding conductor, what phase color is use to mark X2 going to the Split unit disconnect? X1 is Black, X2 is White? Orange stripe marking? Educate me? Thanks..
 
What color would you use to designate the ungrounded conductor on the secondary if black is already designated for something else?
 
X2 is a grounded conductor and should be identified per Art 200.6
Thanks. I was just curious. In all my years, I've never been faced with the opportunity to have to Bond a Single Phase Transformer system with a voltage of 208 from phase to ground on one leg on the secondary. So it kinda puzzled me for a bit as far as the marking. I just wanted to verify it.
 