There is a set of metal sleeves in the concrete slab between the first and second floors. Conduits containing communication wires will be passed through the sleeves. Fireproofing material will be installed in the gap between the outside of the conduits and the inside of the sleeves.
Is there a requirement to bond the sleeves? Would the answer be different if the conduits contained power wires (e.g., 277 volt lighting circuits)?
I looked in articles 250, 645, and 800, and found no answers. Is this really going to boil down to the opinion of the AHJ regarding whether the sleeves are ?likely to become energized??