The electron man
- Nyc
- Electrician
Dose the bonding of the neutral and ground in the main panel have anything to do with a breaker tripping ? Would the breaker still trip if its not bonded ?
Just under 2 years in the trade what is GES ?Assuming you are talking about the GES, it plays no part in clearing faults or overloads.
Yes, if you have a fault to ground on a piece of equipment that has a equipment grounding conductor terminated to it. By bonding them at the Main Service panel it creates a low impedance path through the equipment grounding conductor back to the transformer through the neutral (grounded) conductor so that the overcurrent device clears.Dose the bonding of the neutral and ground in the main panel have anything to do with a breaker tripping ? Would the breaker still trip if its not bonded ?
So my follow up question is , in older homes with no ground what would happen if a hot would touch a metal box ?It depends on what is causing the breaker to trip.
If overload or line-to-line or line-to-neutral fault, no.
If due to a line-to-grounded surface fault, then yes.
So only in a ground fault it won't trip, if its not bonded correct ?Yes, if you have a fault to ground on a piece of equipment that has a equipment grounding conductor terminated to it. By bonding them at the Main Service panel it creates a low impedance path through the equipment grounding conductor back to the transformer through the neutral (grounded) conductor so that the overcurrent device clears.
Grounding Electrode System. You can do away with all the rods, water pipes, building steel, etc .... and the service neutral will clear the fault.Just under 2 years in the trade what is GES ?
The box would become electrically hot.So my follow up question is , in older homes with no ground what would happen if a hot would touch a metal box ?
There is a lot of confusion in the trade about grounding. Article 250 in the NEC is the largest article in the code book. When I first started in the trade I had different Electricians tell me different things about grounding. I found out over the years that a lot of it wasn’t correct. There are some very knowledgeable people on here…..however I think that if you really want to get a good grasp on how the whole grounding system works it would be to buy a book that deals strictly with that. There are books that have a lot of graphics in them that can make it easier to understand. Learn about it now and you will be ahead of the game. You will find out that being an Electrician is a lifetime of learning. Good luck!So only in a ground fault it won't trip, if its not bonded correct ?
This also points out why the EGC should not be connected between grounding receptacles in extensions to GFCI-protected non-grounded circuits. They don't want a fault to the housing of one plugged-in device with a 3-wire cord and plug to energize the housing of another device with a 3-wire cord and plug.The box would become electrically hot.
It sure is a lifetime of learning but I love it , I plan on getting mike holts course on grounding and bonding once I finish the electrical theory course thanks for the helpThere is a lot of confusion in the trade about grounding. Article 250 in the NEC is the largest article in the code book. When I first started in the trade I had different Electricians tell me different things about grounding. I found out over the years that a lot of it wasn’t correct. There are some very knowledgeable people on here…..however I think that if you really want to get a good grasp on how the whole grounding system works it would be to buy a book that deals strictly with that. There are books that have a lot of graphics in them that can make it easier to understand. Learn about it now and you will be ahead of the game. You will find out that being an Electrician is a lifetime of learning. Good luck!
You lost me lol , very new to thisThis also points out why the EGC should not be connected between grounding receptacles in extensions to GFCI-protected non-grounded circuits. They don't want a fault to the housing of one plugged-in device with a 3-wire cord and plug to energize the housing of another device with a 3-wire cord and plug.
Also if you have any book recommendations please shoot them my way thanksThere is a lot of confusion in the trade about grounding. Article 250 in the NEC is the largest article in the code book. When I first started in the trade I had different Electricians tell me different things about grounding. I found out over the years that a lot of it wasn’t correct. There are some very knowledgeable people on here…..however I think that if you really want to get a good grasp on how the whole grounding system works it would be to buy a book that deals strictly with that. There are books that have a lot of graphics in them that can make it easier to understand. Learn about it now and you will be ahead of the game. You will find out that being an Electrician is a lifetime of learning. Good luck!
Suppose you use a GFCI device to allow use of grounding receptacles on a non-grounded circuit. Now, suppose you want to add a receptacle or two. You would use NM cable, which has a ground. You should not connect the ground wires to any receptacles or other ground wires. Clip them off.You lost me lol , very new to this
So I am pretty sure that the equipment ground would still be required to bond all metal parts it enters. Does your state have a requirement to remove the ground wire. Here clipping that wire would get me in a bit of trouble and if I came to a new romex to re feed the old home run with a new grounded circuit to find that I need to completely rewire this new wire because the ground is clipped off I'd be mad. I think there's a mike holt pic showing connecting the ground to the gfi to bond metal boxes after the initial device.Suppose you use a GFCI device to allow use of grounding receptacles on a non-grounded circuit. Now, suppose you want to add a receptacle or two. You would use NM cable, which has a ground. You should not connect the ground wires to any receptacles or other ground wires. Clip them off.
Suppose an internal hot wire energized the external metal parts of a load with a grounding plug. If you connect the ground between two receptacles, the metal parts of a second load with a grounding plug would also become energized, interconnected by the ground wire in the new cable.
See NEC 406.4(D)(2)(b) and (c).Does your state have a requirement to remove the ground wire.
You can't extend at all therefore don't cut the ground you need to add a true ground or nothing at all.See NEC 406.4(D)(2)(b) and (c).