We assemble generators from one meggawatt to two meggawatt using a wye configeration. The voltage can range from 240 volts to 14,400 voltsThey are load tested through a delta to delta transformer then to a resistive and reactive loadbank.
There hasn't been an issue until one day, the video monitor for the test cell was fluctuating more than normal. In trying to locate the problem, I noticed that that there was large amount of current to ground. Further investigation showed that we are bonding the neutral of the generator to the generator housing ground. This was directed by UL and CSA (Canadian Standard Association). The generator was properly grounded for ground protection.
I immediately stopped operations and ohmed the generator, transformer, switchgear and loadbank. Did not find the problem. If I presumed to be correct, is that when we bonded the neutral to ground the ground then became a current carrying conductor. The neutral was not connected to anything but the ground at this point. The procedure was immediately changed to disconnect the bond and test the generator. I was concerned of the potental voltage could have caused personell safety along with equipment.
My question is why does UL specify bonding the neutral with the ground and should this be done in the field verus production. Second, If testing utilizing the neutral has to be done, what meathod should I use. Was there other ways to resolve this other than what I did? I know my recomendations but would very much recieved different views. daniel_jim@cat.com
There hasn't been an issue until one day, the video monitor for the test cell was fluctuating more than normal. In trying to locate the problem, I noticed that that there was large amount of current to ground. Further investigation showed that we are bonding the neutral of the generator to the generator housing ground. This was directed by UL and CSA (Canadian Standard Association). The generator was properly grounded for ground protection.
I immediately stopped operations and ohmed the generator, transformer, switchgear and loadbank. Did not find the problem. If I presumed to be correct, is that when we bonded the neutral to ground the ground then became a current carrying conductor. The neutral was not connected to anything but the ground at this point. The procedure was immediately changed to disconnect the bond and test the generator. I was concerned of the potental voltage could have caused personell safety along with equipment.
My question is why does UL specify bonding the neutral with the ground and should this be done in the field verus production. Second, If testing utilizing the neutral has to be done, what meathod should I use. Was there other ways to resolve this other than what I did? I know my recomendations but would very much recieved different views. daniel_jim@cat.com