I have been asked for an explanation of a grounding (bonding) situation that has been discussed here previously but am interested in any input/clarification so that I may pass it along.
The questions concern fire sprinkler systems and the question is three-fold:
250.52(A) requires underground metal piping systems to be used as grounding electrode with no particular reference to fire sprinkler systems in the NEC as far as I can determine.
It is my understanding that the sprinkler code (??) prohibits the system to be used "for grounding" (years ago when I had that Code available the wording was that "for grounding" not as an electrode..fine line).
So, do we address the metal underground fire sprinkler piping as required by 250.52(A) or not ?
Secondly 250.104 requires metallic piping systems be bondedl. If we don't follow 250.52 do we also exempt fire sprinkler systems from the 250.104 requirement,.
Third: Do the "groved couplings", where used, electrically isolate the sections of piping (sprinkler or other systems).
The questions concern fire sprinkler systems and the question is three-fold:
250.52(A) requires underground metal piping systems to be used as grounding electrode with no particular reference to fire sprinkler systems in the NEC as far as I can determine.
It is my understanding that the sprinkler code (??) prohibits the system to be used "for grounding" (years ago when I had that Code available the wording was that "for grounding" not as an electrode..fine line).
So, do we address the metal underground fire sprinkler piping as required by 250.52(A) or not ?
Secondly 250.104 requires metallic piping systems be bondedl. If we don't follow 250.52 do we also exempt fire sprinkler systems from the 250.104 requirement,.
Third: Do the "groved couplings", where used, electrically isolate the sections of piping (sprinkler or other systems).