xguard
Senior Member
- Location
- Baton Rouge, LA
I have a pull box ahead of a service disconnect. There are no splices in the pull box. The box is connected to the disconnect with RMC. In order to bond the box to the Grounded Service Conductor, is it permitted to run a conductor (sized based on 250.66) from the Neutral Bus in the Service Disconnect back to the pull box and attach it with a lug?