Senior Member
Wondering if I need to bond my metal box with grounding installed in PVC raceway, if used as a pull-box? (pull through - no splicing)
 
314.4 Metal Boxes
Metal boxes shall be grounded and bonded in accordance with Parts I, IV, V, VI, VII, and X of Article 250 as applicable, except as permitted in 250.112(I).
250.4 General Requirements for Grounding and Bonding
(A) Grounded Systems. (2),(3),(4)
 
Wondering if I need to bond my metal box with grounding installed in PVC raceway, if used as a pull-box? (pull through - no splicing)
Box is required to be bonded... period.

If you want to pull through all your EGC's, you can. However, then you'd have to run a separate bonding jumper to ground the box.
 
Wondering if I need to bond my metal box with grounding installed in PVC raceway, if used as a pull-box? (pull through - no splicing)

Just strip back a little of the Insulation on the EGC and use a "Lay-in" lug and bond it to the box.
 