maintenceman
Member
- Location
- Ohio
Ok so I have a question, stay with me here lol. This question is solely on the bonding of the service for the building. I know the answer I think, but want to hear it from someone else.
1. Building has been added on to twice, so there all one building but added to 2 times.
2. service comes into building now (into the 2nd and most recent addition) to a 800a transfer switch. In transfer switch the nuetral is bonded to cabinet
3. out of TS, is parallel feeds to generator for TS, and (2) parallel feeds to loads. One new panel and one feed to old existing service. New service feed (addition #2) is right next to TS and is fine I think. Old service (original building and addition #1) is about 200' away and is fed with parallel feed, but only has 3 hots and a ground in the pvc's feeding it (no ground)
4. The new service is fine, grounds and nuetrals seperated in panels, etc (Addition #2 to building)
5. Old service that is 200 or so feet away is fed to an MCC where the nuetral, grounds, water ground and ground rod are all bonded together.
6. Then out of MCC it feeds the original building service, which is (2) 200a disc. Each of these disconnects are also bonded inside
7. So in turn, the nuetral is bonded in 4 different places!
So since the newest addition (I did not work here then)we have have had some problems with computers and electronics going bad and quitting randomly. So 2 questions that I think I know the answers to.
1. Is this bonding legal somehow?
2. Could this bonding be causing problems with electronic devices in building?
Thanks for replies and sorry if its confusing the way I have wrote it out
1. Building has been added on to twice, so there all one building but added to 2 times.
2. service comes into building now (into the 2nd and most recent addition) to a 800a transfer switch. In transfer switch the nuetral is bonded to cabinet
3. out of TS, is parallel feeds to generator for TS, and (2) parallel feeds to loads. One new panel and one feed to old existing service. New service feed (addition #2) is right next to TS and is fine I think. Old service (original building and addition #1) is about 200' away and is fed with parallel feed, but only has 3 hots and a ground in the pvc's feeding it (no ground)
4. The new service is fine, grounds and nuetrals seperated in panels, etc (Addition #2 to building)
5. Old service that is 200 or so feet away is fed to an MCC where the nuetral, grounds, water ground and ground rod are all bonded together.
6. Then out of MCC it feeds the original building service, which is (2) 200a disc. Each of these disconnects are also bonded inside
7. So in turn, the nuetral is bonded in 4 different places!
So since the newest addition (I did not work here then)we have have had some problems with computers and electronics going bad and quitting randomly. So 2 questions that I think I know the answers to.
1. Is this bonding legal somehow?
2. Could this bonding be causing problems with electronic devices in building?
Thanks for replies and sorry if its confusing the way I have wrote it out