madchad

Member
Location
Columbia, MD USA
Somewhere in the NEC I thought read an article that stated you must use bond bushings on any raceway 1-1/4" and larger and over 250v regardless of the knockouts (punched,eccentric,concentric). Does anyone have info about this requirement? If it even exists. :confused:
 
Re: Bonding raceways over 250v

Requirements for bonding circuits operating at over 250 volts to ground are in 250.97. These apply to all conduit, not just 1?" or larger.
 