:-?Where is it required by code to bond the rebar in a residential footing?

Your never required to bond rebar by the NEC, but if 1/2" or larger rebar, 20' or longer exists in the footing the NEC requires you use it as a grounding electrode. See 250.50 and 250.52(A)(3)
 

wbalsam1

Senior Member
Location
Upper Jay, NY
:-?Where is it required by code to bond the rebar in a residential footing?
It's as iwire has pointed out with the possible exception being if you're still on the 2002 NEC the wording at 250.50 says "if available" which is a lot different than the '05 which says "where present".:smile:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Check out the sections that Bob posted. Chances are very good that you'll need a CEE in any new building even a residential dwelling.
 

electricmanscott

Senior Member
Location
Boston, MA
Check out the sections that Bob posted. Chances are very good that you'll need a CEE in any new building even a residential dwelling.

Is there typically rebar in resi foundations in your area?

There never seems to be any on the houses I wire. I always try to get #4 in there anyway to avoid ground rods.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Is there typically rebar in resi foundations in your area?

There never seems to be any on the houses I wire. I always try to get #4 in there anyway to avoid ground rods.


There is always some reinforcement in the footing. I have seen some #3 rebar which would eliminate the requirement for a CEE.
 