Bonding RGS w/meyers hub to pullbox

Status
Not open for further replies.

yellow77

Member
I am installing a 1600A. backfeed system connecting to the buss of an existing 1600A. protected MDP. RGS (Rigid Galv. Steel) will be installed from the MDP to a pull box connected by weatherproof gasketed hubs, then to the new enclosed breaker. This is for a temp Generator to be connected. I know I need grounding bushings on both sides, but do i need a means of bonding inside the pullbox? Thanks
 
Unless you entering concentric KOs I see no NEC reason you need any grounding bushings at all.

If you would like to include additional grounding means you can get myers hubs with grounding lugs on them.
 
And if you need a bonding connection for some reason, they make the hubs with grounding lugs on them so you can add a bonding jumper.
 