Hey guys could use your input on this.
Scenario: School campus with multiple buildings and service utility transformers.
I have a new classroom building that is being served by a new dedicated, utility transformer. This building is on a school campus with multiple buildings where each building has its own service utility transformer and its own grounding electrode system.
The plans reviewer has requested us to run a #3/0 bare conductor to connect the new building?s GES to the neighboring existing building?s structural steel. His argument is that the service transformer is an SDS and requires common electrodes to be bonded together. My thoughts are this is not an SDS and per definition of an SDS, it specifically states the words "other than service". His other reason is that there are copper communications, fire alarm lines, and an exterior metal canopy that connect the 2 buildings together where a lightning strike could cause equipment damage.
Would it hurt to bond a separate building to the new building?s GES? Wouldn?t a short circuit in one building travel next door to the other building?s GES?
Thanks for your help.
Scenario: School campus with multiple buildings and service utility transformers.
I have a new classroom building that is being served by a new dedicated, utility transformer. This building is on a school campus with multiple buildings where each building has its own service utility transformer and its own grounding electrode system.
The plans reviewer has requested us to run a #3/0 bare conductor to connect the new building?s GES to the neighboring existing building?s structural steel. His argument is that the service transformer is an SDS and requires common electrodes to be bonded together. My thoughts are this is not an SDS and per definition of an SDS, it specifically states the words "other than service". His other reason is that there are copper communications, fire alarm lines, and an exterior metal canopy that connect the 2 buildings together where a lightning strike could cause equipment damage.
Would it hurt to bond a separate building to the new building?s GES? Wouldn?t a short circuit in one building travel next door to the other building?s GES?
Thanks for your help.