No Code. The resistance between two grounds is proportional to the inverse of the distance.
The one exception I know of is that in mines the substations are normally grounded with two grounds. The HV side, fences, lightning arresters, frame, etc., are tied to one ground. A second ground at least 25 feet away goes to the transformer neutral and supplies the neutral and grounds for the mining equipment (LV) side. This is done to prevent power line disturbances and lightning entering the mine.
You want the grounds to be far enough apart to avoid near field coupling (one or two ground rod lengths) but not so far that it becomes remote Earth.
Regardless why would you be concerned with coupling? If we have two transformers the return path on a fault is back to the source (complete the circuit).