2017 NEC 250.92 (B) (Services) says that "bonding jumpers shall be used around impaired connections...oversized, concentric, or eccentric knock-outs. Standard locknuts or bushings shall not be the only means of bonding required by this section but shall be permitted to be installed to make mechanical connection of the raceway(s)"
So, when you have a metallic nipple that goes between the meter box and the box that houses the first means of disconnect, and there are no knock-outs left, the hole is not oversized, and the nipple is fastened with standard locknuts only, would it be considered to be bonded since there are no knock-outs or reducing washers?
Or is it not considered to be bonded because you used standard locknuts as your connection to the box? There is a period between the sentence talking about impaired connections, and the sentence talking about standard locknuts as a means of bonding, and a sentence is a group of words that expresses a complete thought.
The AHJ I work for has only been requiring bonding jumpers around impaired connections, but we have been discussing it internally and we are wondering if a strict reading of the code means me need to always have a listed bonding connection on service nipples, even when there are no knock-outs left and the hole is not oversized.
Any insight you guys have will be appreciated.
So, when you have a metallic nipple that goes between the meter box and the box that houses the first means of disconnect, and there are no knock-outs left, the hole is not oversized, and the nipple is fastened with standard locknuts only, would it be considered to be bonded since there are no knock-outs or reducing washers?
Or is it not considered to be bonded because you used standard locknuts as your connection to the box? There is a period between the sentence talking about impaired connections, and the sentence talking about standard locknuts as a means of bonding, and a sentence is a group of words that expresses a complete thought.
The AHJ I work for has only been requiring bonding jumpers around impaired connections, but we have been discussing it internally and we are wondering if a strict reading of the code means me need to always have a listed bonding connection on service nipples, even when there are no knock-outs left and the hole is not oversized.