electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
Say I have service enclosure A that is properly bonded. I run a rigid nipple from A to service enclosure B, a pull box that needs to be bonded. If I have a bonding locknut on both sides of the nipple(one in each enclosure, regular locknuts on the outsides), does that take care of the service bonding requirements for box B? My vote is this is ok.