I’m meeting some clarification on article 250.92B… I have 3” parallel raceways leaving a disconnect and feeding a 800 amp panel 200 feet away, Both the disconnect and service panel holes for the raceways were punched out. Is a lockring and plastic bushing enough to meet the bonding requirement of the raceways or is a bonding bushing also needed?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sounds like this is a feeder after the service disconnect? If so no additional bonding beyond the standard locknuts is required.

Welcome to the Forum. :)
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A service raceay (a raceway containing service cocnductors) would require bonding beyond a standard locknut.
 