Bonding service

Status
Not open for further replies.

SAP

Senior Member
Location
Fresno Ca
I have a underground service ran in PVC pipe, I have to swap out panel "service change" existing is a old zinsco ,Knock out for service is right in the middle of existing panel, I'm putting in a side by side new main, I need to move my PVC service conduit a few inches to the left, parts house does not have the PVC offsets, only the aluminum ones, if I use the aluminum offset do I have to bond it to panel thank you
 

iwire

Moderator
Staff member
Location
Massachusetts
I have a underground service ran in PVC pipe, I have to swap out panel "service change" existing is a old zinsco ,Knock out for service is right in the middle of existing panel, I'm putting in a side by side new main, I need to move my PVC service conduit a few inches to the left, parts house does not have the PVC offsets, only the aluminum ones, if I use the aluminum offset do I have to bond it to panel thank you

Yes it would have to be bonded.

It might also be a listing violation.
 

kwired

Electron manager
Location
NE Nebraska
Is it emerging from dirt or from concrete? Just dig it out and move it over if possible or else find or make something to bend it with. Blanket type heaters may allow you to bend it in place.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Recently i had a similar install that I cut back the PVC as far as I could and installed a new offset piece.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Not where I can verify right now but I believe offsets are listed for nipples BETWEEN BOXES
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
and to add fuel to then fire, I recall a question about offset nipples being used where higher fault currents are available such as services.
 