NO
NO
Here is a reply from the NFPA on this situation that would apply if we are talking about a hydromassage bathtub.
From: Jeffrey Sargent, NFPA Senior Electrical Specialist
Date: 9/13/05
The isolated metal stem for the faucet that is associated with the water supply for the hydromassage bathtub does not constitute a metal water piping system nor is it a grounded metal part, therefore it is not required to be bonded. Section 680.74 requires bonding of metal water piping systems and grounded metal parts associated with the hydromassage bathtub and the isolated metal stem for the faucet is not covered by the bonding requirement.
This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author, and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should be relied upon, to provide professional consultation or services.