I recently inspected a large house with attached guest house. The service panel is on the exterior of the guest house. There are 2 branch panels next to each other in the house.
The guest house is attached to the house via roof and patio / slab.
I called out the ground / neutral bond straps in place in the branch panels and said they should be removed. Here is the response from the electrician:
"As for the removal of the ground neutral jumper bar a determination [was made] by the county inspector and myself during construction to treat the project as two separate structures. The installation is correct per the NEC with the grounds and neutrals tied together as well as a new ufer located at the subpanels and new gas and water bonds."
I still think this is incorrect. Any opinions?
The guest house is attached to the house via roof and patio / slab.
I called out the ground / neutral bond straps in place in the branch panels and said they should be removed. Here is the response from the electrician:
"As for the removal of the ground neutral jumper bar a determination [was made] by the county inspector and myself during construction to treat the project as two separate structures. The installation is correct per the NEC with the grounds and neutrals tied together as well as a new ufer located at the subpanels and new gas and water bonds."