KentAT
Senior Member
- Location
- Northeastern PA
I was asked this question and I cannot answer it.
Does the practice of sleeving a structural steel grounding or bonding jumper through a poured concrete slab (using PVC SHC40 conduit for protection) violate any NEC code when leaving the interior of a Class1, Div 1 or 2 area? The jumper is typically attached to the plant's ground loop that is running throughout the plant. The point of connection is U/G, usually within 10 feet or so of the building walls.
I would think that there is no issue, but I can't answer "why" when someone brings up the question of sealing between the Div 1 interior and the unclassified U/G location of the tie-in.
Plant is a natural gas compressor station.
Kent
Does the practice of sleeving a structural steel grounding or bonding jumper through a poured concrete slab (using PVC SHC40 conduit for protection) violate any NEC code when leaving the interior of a Class1, Div 1 or 2 area? The jumper is typically attached to the plant's ground loop that is running throughout the plant. The point of connection is U/G, usually within 10 feet or so of the building walls.
I would think that there is no issue, but I can't answer "why" when someone brings up the question of sealing between the Div 1 interior and the unclassified U/G location of the tie-in.
Plant is a natural gas compressor station.
Kent