Bonding Structural Steel to Ufer Ground

Status
Not open for further replies.

DaveSeitz

New member
Location
Bentonville, AR
Refering to Art 250.104(C) - If the structural steel is bonded to the main electrical service panel according to table 250.66 and the Ufer ground is bonded to the service with #4; if we bond the Structural steel to the Ufer ground in addition to this, what size wire is needed?.
 
Last edited:
While the Ufer gound is only required to have a #4 wire back to the service, according to 250.104 C the bonding jumper from the steel to one or more grounding electrodes used must be sized per table 250.66.
 
Dave, please do not edit your posts after someone has repied to them.

Thanks

Roger
 